OK Lec, I understand the comment about High Impedance now, if you'll pardon the pun, we appear to have got our wires crossed
I see where your coming from with the concern regarding the enclosure, however if the protective device were a time delayed RCD proporly rated for the installation and role it will play in it, then there should not be an increased risk of shock.
Lets use this TT system as the basis for this discussion.
We have the Head, probably with a 100A BS1361 Fuse inside, the Main Service Bond is via an Earth Stake in the grounds of the premises and this currently connects the Stake to the Consumer Unit, now lets introduce a New Consumer Unit and update the installation for compliance with BS7671:2004.
As per Regulation 542-04-01 we shall install a Main Earthing Terminal and from this I shall install a New Main Equipotential Bond to the Earth Stake, which I would test initially to ensure compliance and where possible reduce the impedance of the stake. This new Bond would be 25mm 6491X single core copper cable. The Regulations allow the use of 16mm, but the reduced impedance of the 25mm will increase safety slightly, and all gains that can be made in a TT system are worth every effort.
From the Main Earth Terminal, I would then run a 25mm Bond to the Consumer Unit Main Earth Terminal, again to keep the impedance as low as possible. The Metal Enclosure you mention I would install unless absolutely unavoidable, I would install an Insulated unit, however I would install a 25mm bond from the Earth Terminal in the enclosure, metal or insulated, back the the Main Earthing Terminal. Also from the Main Earthing Terminal I would install 16mm Bonds to the Water Service and Gas if any existsed in the premisises.
Now for the Main setup. The Consumer Unit I would install would be a split load unit, very similar to what we have installed in the installtion I spoke of in my earlier posts.
All sockets and power using circuits would be protected by a main switch with a 80A 30mA Time Delayed rating. On the other side of the board I would install a 63A Isolator feeding ONLY the intieror lighting circuits of the installation. These lighitng circuits being protected by Type B MCB's of a rating as near to the design current of the circuit as is possible. In a small rural property it is possible to install a 3A MCB for a Lighting circuit due small number of lights on the circuit. Simply installing a 6A as it's what we normally do is not always best practice.
The Isolator to be installed between the meter and the Consumer would would be a 500mA 100A Time Delayed RCD.
I am aware that many will say that the Regs say the Main switch should be a 30mA RCD, however all truly vulnerable circuits are protected by such a device in the main consumer unit, and further, such an installation does comply.
My personal thinking is that putting lighting circuits on RCD's is potentially more dnagerous than not putting them on it. The chances of a person getting a fatal shock from a lighting circuit are much lower than the chances of the main RCD being operated by a minor fault on another circuit or more likely nuisance tripping from other influences.
In such an installation I have always ensured that any socket which may be used to feed externally to the building are MK RCD protected units, thus reducing the risk of main switch tripping even further, as it is often lawn mowers etc that cause such faults in domestic premises in my experience, yours may be different. Further on TT systems, which are abundant where I live, I have never allowed an Earth stake to have a reading above 50 Ohms. I know that the Regs say a much higher figure is permissable, but I feel happier with this reduced figure.
This is my take on things, I appreciate others may disagree.