firstly, correct or incorrect is in the eye of the beholder.
secondly I'm at my mothers so don't have access to me regs book but I'm pretty sure that this is an accurate definition..
please note the words in italics.
now..
there are a few words in your post that I would like to point out..
this is not to say that it doesn't need supplimentary bonding in areas such as bathrooms to meet the requirements of other regulations..
while there is no harm in putting a 10mm earth and a clamp on the copper, it's not absolutely needed.. you couldn't automatically mark it down on a PIR for not having one for example..
take as an example the pipes for your rdiators, do you run a main bond back to the MET for those?
you don't even have to cross bond them at the boiler for electrical regs ( but the gassafe guys seem to like to do it so it might be in their regs to do so )..
secondly I'm at my mothers so don't have access to me regs book but I'm pretty sure that this is an accurate definition..
An Extraneous Conductive Part is a metal part that is not part of, but in proximity to the electrical installation and is liable to introduce earth potential.
please note the words in italics.
now..
there are a few words in your post that I would like to point out..
it's a guide to, not a definitive cast iron explanation of the regs..Outlined below is the relevant section from the Electricians guide to the Building Regulations:
that's MAY be needed.. if it tests as extraneous supply ( maybe it's only 500mm of plastic because the entry point moved etc.. ) then it needs main bonding, if it's NOT extraneous then it doesn't."There is NO requirement to main bond an incoming service where both the incoming supply pipe and the pipework within the installation are both of plastic. Where there is a plastic incoming service and a metal installation within the premises , main bonding may be needed and in such cases the main boding conductors should be connected on the customers side of any meter, main stop cock or insulating insert."
this is not to say that it doesn't need supplimentary bonding in areas such as bathrooms to meet the requirements of other regulations..
while there is no harm in putting a 10mm earth and a clamp on the copper, it's not absolutely needed.. you couldn't automatically mark it down on a PIR for not having one for example..
take as an example the pipes for your rdiators, do you run a main bond back to the MET for those?
you don't even have to cross bond them at the boiler for electrical regs ( but the gassafe guys seem to like to do it so it might be in their regs to do so )..