Ecotec Plus 831 switching itself on

Very useful, thank you. Will give it a further test tomorrow morning and see how I get on!
 
Sponsored Links
3. If the pipe-stat is located in a very cold position where the ambient temperature is only a couple of degrees, that may have a cooling effect on it.

Adding some insulation, around the entire stat and pipe will have it reacting quicker, and more accurately..
 
Think it all seems to be working now. I've reduced the pipe stat to around 5 degrees and it seems to be shutting down now within about 20 mins of the frost protection kicking in. I added some lagging around the stat as recommended also.

Many thanks for all your help on here!
 