So I've given it 20mins, and it seems to be be behaving itself, as in the FT is as it should be.
S.04 Heating mode: Burner on
D.00 Partial load - Automatic
D.005 Flow temp target value - 45deg
D.014 Target Pump speed - not shown
D.015 Actual Pump speed - 86%
D.017 Flow or return temp control - Flow temperature control
D.018 Pump operating mode - Eco
D.040 Flow temp - 45deg
D.041 Return temp - 37deg
I think you should keep a eye on this boiler as it too does not seem to be performing as I would expect in constant pressure mode.....
D170 set to 2. (Bypass dP constant)
D.171 set to 200mbar (Target pressure level value). which I presume you checked.
don't know how many rads you've got but my 10 rad system flows 15.0LPM @ 3.0M (oil fired boiler with practically no pressure loss through its heat exchange, your Gas fired will lose ~ 2.6M @ 21.5LPM through its heat exchanger and doing a few calcs based on a system loss of 3.0M @ 15.0LPM and 3.0M @ 20.0LPM then the circ pump should have only been running at ~ 62% @ its CP SP of 200mbar, 2.0M, flowrate ~ 10.3LPM, or a max of 65% pump speed, flowrate ~ 12.5LPM, (depending on your system loss)
You noted a pump speed of 86% which means the pump was flowing 14.5LPM @ 3.9M or 16.5LPM @ 3.5M (depending on your system loss) no way near its 200mbar SP.
You could reduce D.171 to 150mbar and maye finally to 100mbar after taking a set of readings, however, because its a combi, this might affect the DHW output, so maybe just look at the pump speed as is on CH, change over to a high DHW demand and see does the pump speed stay the same before doing (if) anything.
These pumps can also be run in fixed speed mode but again don't know if this is overridden in DHW mode.