I don't believe that's quite correct.
An isolator is designed to safely break the load, but not to make it.
No, they are only designed to carry the load, not make or break it whilst the load is enabled.
I don't believe that's quite correct.
An isolator is designed to safely break the load, but not to make it.
I don't believe that's quite correct.
An isolator is designed to safely break the load, but not to make it.
Whilst that might be an understandable state of affairs (although not all that 'safe' since, in an emergency, people are quite likely to use a nearby isolator as a means of 'emergency switching'), as has been implied, it does not seem to be how BS7671 sees the situation. Virtually all of the devices listed in Table 537.4 as being suitable as a means of isolation are also indicated to be suitable for 'emergency switching' (which implies the ability to break a circuit under load) - which, in turn, implies that the relevant product Standards (as specified in the Table) require the devices to be capable of breaking cir circuits under load.No, they are only designed to carry the load, not make or break it whilst the load is enabled.
That is, indeed, how BS7671 defines a 'disconnector'/'isolator'.John, BS7671 says:
Disconnector. A mechanical switching device which, in the open position, complies with the requirements
specified for the isolating function.
NOTE 1: A disconnector is otherwise known as an isolator.
NOTE 2: A disconnector is capable of opening and closing a circuit when either a negligible current is broken or made,
or when no significant change in the voltage across the terminals of each pole of the disconnector occurs. It
is also capable of carrying currents under normal circuit conditions and carrying for a specified time current
under abnormal conditions such as those of short-circuit.
in an emergency, people are quite likely to use a nearby isolator as a means of 'emergency switching'),
It is.What Table 537.4 is saying is that if you pick a switch to a particular other BS EN standard, then it may provide the functions of both isolation and emergency switching.
Agreed - it does not literally state that. However, unless there are some relevant Standards for isolators (or 'isolation switches' or 'disconnectors' or whatever) other than those mentioned in that Table, then it is effectively saying that anything which satisfies the requirements for an isolator is also acceptable as an emergency switch, isn't it?What it does not say is that an isolation switch is automatically also an emergency switch, which is what was being partially claimed.
That's certainly of situation which would satisfy that requirement. However, as I said, as far as I can make out, it would also be satisfied by a DP switch which precisely simultaneously broke both poles, since there would never be more than a negligible pd across the contacts of either pole, wouldn't it?The part about voltage simply means that you may use the switch in the additional case that the source voltage is already off (maybe by MCB), or not being drawn from (sinking device is already switched off itself).
Exactly, which is why the nearest 'switching device' (which will not correspond to what you describe) is what will be used in emergency situations in a domestic environment.In a properly designed system the Emergency Stop disconnect should be by means of a Forced Break Contactor. This type of contactor forces the contacts apart by forcing an insulator between the contacts to prevent arcing and to break any weld that may have happened previously . Not really economical for domestic installations.
I'm certainly not 'arguing' - I'm merely reporting what BS7671 says.What are you all arguing about?