Albert said:excuse me for being picky, the load of the shower should be divided by 230..
The iee still use 240v in its calculations
Albert said:excuse me for being picky, the load of the shower should be divided by 230..
Ah well - I'll join you.Albert said:excuse me for being picky, the load of the shower should be divided by 230..
Funny you should ask....Albert said:Do you have a link..ban-all-sheds said:I prefer Swarfega wrestling myself....
Although you might measure or read 240V or even 245V, the theoretical calculations have to be based on 230V. This is not a question of good or bad, this is how it is done. Interestingly you take the load from the sticker as is, of course it might (not necessarily) change the cable size.ban-all-sheds said:Ah well - I'll join you.Albert said:excuse me for being picky, the load of the shower should be divided by 230..
In being picky, I mean.
The headline rating of showers is invariably given for a 240V supply (which de facto ours still is). So if you want to use 230V for your calculations, you need to rummage in the small print where you'll find that what you thought was an 8.5kW shower has just become a 7.8kW one...
Yes, but if you do that then to get an accurate answer you have to use the rating of the shower at 230V, not 240V.Albert said:Although you might measure or read 240V or even 245V, the theoretical calculations have to be based on 230V. This is not a question of good or bad, this is how it is done.
Err.... no.I don't see how the load of the shower relats to the supply, you can supply a 10KW load with 230V, 260V or 200V. This does not change the load it will always be 10KW.
ban-all-sheds said:Yes, but if you do that then to get an accurate answer you have to use the rating of the shower at 230V, not 240V.Albert said:Although you might measure or read 240V or even 245V, the theoretical calculations have to be based on 230V. This is not a question of good or bad, this is how it is done.
Err.... no.I don't see how the load of the shower relats to the supply, you can supply a 10KW load with 230V, 260V or 200V. This does not change the load it will always be 10KW.
Try Ohm's Law.
If we simplify, and ignore the difference in the impedance of the load at different temperatures, then of course it relates to the supply!
Lower voltage = less current = fewer watts.
A shower which dissipates 8.5kW at 240V will dissipate 7.8kW at 230V.
Of course it willAlbert said:You saying that if I have to supply a 100W bulb with 240V, it will consume less watts if we supply with 230V?
Yes - so you change the voltage, and Mr Ohm changes the current, so between you you have changed the power, as P=V*I.Power/voltage = Current. this is a fixed load the maximum demand is (we can say) fixed, the voltage is fixed (whether it is 240 or 230V) so only the current can change when the voltage changes.
Yes, but you can't keep the power the same by somehow pushing more current through it to compensate for a lower voltage.W=I2 * R > R=Constant (not considering changes in temperature as it will effect any supply value) The maximum power needed to oprate this unit is constant, the only parameter that can change is the current demand. that is why I said that it might require a differnt cable size (or not).
Spark123 said:Is it not 7.5kW?
I inconsistently said:So a shower rated at 8.5kW on a 240V supply will at 230V dissipate (8.2 x 230²)/240² = 7.8kW
Nothing else makes sense.Albert said:I think that I know where we miss each other, you are talking about the power that the load will 'use' if the voltage will be reduced to 230V.
But showers don't work like that. If you reduce the supply voltage you cannot reduce the resistance of the heater to compensate. And until they start making showers with SMPSUs in them they will not draw more current when the voltage drops, they will draw less.I am talking about what will you do to get a certain load to be used fully in the event that the voltage is lower you will have to supply or it will draw more current.
Absolutely not.This is an academic argument because the way to design the circuit is to take the maximum load on the unit and divide by 230V
It is officially allowed to rise to 253V.which is the official level of voltage in this country (although in reality it can be 240V or even 245V).
I know, but you don't use it for design purpose, you would use 230V.It is officially allowed to rise to 253V.
I don't know - I've never eaten Swarfega.blueblob said:IS CUSTARD BETTER THAN SWARFEGA!!!!!
If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.
Select the supplier or trade you require, enter your location to begin your search.
Are you a trade or supplier? You can create your listing free at DIYnot Local