Why you say 20 amps was thinking 32 amp for main fuse ?
I gathered it was 20 amp for a 2.5 radial and 32 amp for a 2.5 ring circuit.
2.5mm SWA is not rated for 32amps.
If you mean, quote two different posts in one reply, then you have to hit reply to one post, copy the text, then go back and hit reply to the other post before pasting the first lot of quoted text in before or after the second lot. It's help if you use the "open in new tab" function of the browser so you can :Sorry for double post do not know how to do one with the quotes.
2.5 is 'usually' OK for a ring (Ring Final Circuit, RFC). That's on the basis that normally the load would be distributed around the ring, and so share the two parallel paths back to the distribution board - so in principal it shouldn't be possible to overload one leg if the circuit is properly designed.I was not saying 2.5 was rated 32 amps I was saying it was protected with the next fuse up 32 amps ?
This is what 2 of my properties are and I have read is ok for ring but gold told no.
Yes, but how can you "protect" a cable rated at less than 32A with a 32A device?2.5mm SWA is not rated for 32amps.
Sorry for double post do not know how to do one with the quotes. I was not saying 2.5 was rated 32 amps I was saying it was protected with the next fuse up 32 amps ?
No, you weren't told that.This is what 2 of my properties are and I have read is ok for ring but gold told no.
That's not a ring.I was thinking of connecting 2.5mm SWA cable to the T & E in the loft then running it down my house and burying underground to the shed.
If the fuse on that 10mm is 40amp then you can not connect 2.5mm cable to it.
The fuse would have to be reduced to 20 amp at the most.
But your single run from the house to the garage is not a ring.Why you say 20 amps was thinking 32 amp for main fuse ?
I gathered it was 20 amp for a 2.5 radial and 32 amp for a 2.5 ring circuit.
Yes, but how can you "protect" a cable rated at less than 32A with a 32A device? With a ring which is what I was implying very early on in the thread.2.5mm SWA is not rated for 32amps.
Sorry for double post do not know how to do one with the quotes. I was not saying 2.5 was rated 32 amps I was saying it was protected with the next fuse up 32 amps ?
- //www.diynot.com/wiki/electrics:mcbtocable
- http://www.tlc-direct.co.uk/Book/4.3.1.htm
- http://www.tlc-direct.co.uk/Book/4.3.11.htm
- http://www.tlc-direct.co.uk/Book/5.3.1.htm
- http://web.archive.org/web/20080213151445/http://www.kevinboone.com/cableselection_web.pdf
- http://www.tlc-direct.co.uk/Technical/Charts/VoltageDrop.html
No, you weren't told that.This is what 2 of my properties are and I have read is ok for ring but gold told no.
That's not a ring.I was thinking of connecting 2.5mm SWA cable to the T & E in the loft then running it down my house and burying underground to the shed.
If the fuse on that 10mm is 40amp then you can not connect 2.5mm cable to it.
The fuse would have to be reduced to 20 amp at the most.
But your single run from the house to the garage is not a ring.Why you say 20 amps was thinking 32 amp for main fuse ?
I gathered it was 20 amp for a 2.5 radial and 32 amp for a 2.5 ring circuit.
I wrote this very early on.
Why you say 20 amps was thinking 32 amp for main fuse ?
I gathered it was 20 amp for a 2.5 radial and 32 amp for a 2.5 ring circuit.
Cable distance is 18 meters tops.
Supply is 240v.
Thanks for reply
Read more: //www.diynot.com/forums/electrics/electric-to-log-cabin.344050/#ixzz2CTSLYczJ[/QUOTE]
You can't even be rsed to remove that last line that the site inserts when you copy and paste a post, can you.
Anyway...
In my loft I have a 10mm T & E cable isolated which runs to the fuse board on a 40amp fuse. I was thinking of connecting 2.5mm SWA cable to the T & EIf the fuse on that 10mm is 40amp then you can not connect 2.5mm cable to it.
The fuse would have to be reduced to 20 amp at the most.First of all, he explained why he said 20A, it's because you'd said that you were going to connect a 2.5mm² cable to the 10mm² cable which is on a 40A breaker.Why you say 20 amps was thinking 32 amp for main fuse ?
Secondly, you had not said that you were thinking of changing that 40A breaker to a 32A one. But if you had, that would also have been wrong.
It is, but you had not been talking about a ring, you had been talking about the radial to the shed, and as you had been talking about a 2.5mm² radial that is why you were told that it had to be on a 20A fuse.I gathered it was 20 amp for a 2.5 radial and 32 amp for a 2.5 ring circuit.
And there you went again, talking about the radial to the shed.Cable distance is 18 meters tops.
Nobody has told you that 32A is wrong for a 2.5mm² ring final. Nobody.
You gave no evidence of having understood it, and lots of evidence that you didn't get what people were telling you.Which is basically saying I understand 32 amp is for a ring and 20 amp is for a radial either way I understood it.
Even now the fact that you are still banging on about having been told that 32A for a 2.5mm² ring is wrong shows that you don't understand what you are writing or what you are reading.
Wrong - you had got onto designing it, and your first design was to put a 2.5mm² cable on a 40A breaker.Again I said I gathered it was 20 amp for a 2.5 radial and 32 amp for a 2.5 ring circuit. I had not even got onto designing the circuit at this stage
I suggest you accept the fact that you really do not have a good enough understanding of all of this to be DIYing, and let that electrician do it all for you.either or I have confirmed what I knew with a spark and he has confirmed it to be correct .
We're still waiting.wait I will find where I said earlier for ring and got told no .
I've been trying to make some sense of what the OP has been saying. Is it possible that one of his confusions is that he thinks (obviously incorrectly) that if 2.5mm² is OK for a 32A ring, then it should also be OK for a (single) cable 'feeding' that ring?We're still waiting.wait I will find where I said earlier for ring and got told no .
I've been trying to make some sense of what the OP has been saying. Is it possible that one of his confusions is that he thinks (obviously incorrectly) that if 2.5mm² is OK for a 32A ring, then it should also be OK for a (single) cable 'feeding' that ring?We're still waiting.wait I will find where I said earlier for ring and got told no .
Kind Regards, John