Thanks. At first sight that appears to be a very clear answer to the question I was asking. However, when I start thinking a bit more (always dangerous!), I'm not so sure that it all makes complete sense. I obviously have no problem with a desire to 'ensure that an accessory is safe to use before being put into service', but I'm struggling to decide in what sense, for example, a replacement (non-metallic) lighting switch would/could be unsafe to put into service without undertaking those tests (even once one has decided how to undertake them on a light switch!)?This issue was covered in issue 172 of NICEIC's Connections magazine.Replacement of accessories The replacement of an accessory, such as a socket-outlet, ceiling rose or lighting switch, on a like-for-like basis may be regarded as maintenance rather than installation work.
However, NICEIC expects 'Approved Contractors, Conforming Bodies and Domestic Installers undertaking such maintenance work to carry out essential inspection and testing to ensure that the replacement accessory is safe to use before being put into service.
As a minimum, tests to confirm that shock protection has been provided are essential. These essential tests are:
:- a test to establish the earth fault loop impedance [the value of which needs to be,checked against the characteristics of the protective device)
:- polarity, and
:- where an RCD is used for fault protection or addition protection, the correct operation of the RCD.
Kind Regards, John.