what do i do next.
the story so far.
1,had plumber changed all my rads fo newer and larger rads,no probs there.the plumber a corgi reg chap did a visual inspection of the boiler and was conserned about fumes.he took off front panel and used his tpi co meter and found co reading around where burner meets combustion box.he said readings was same as putting tpi meter down flue.
he asked me to discon it i agreed.signed his paperwork etc.
2.called british gas in as under maintaince contract.
bg engineer reconnects boiler restarts it and says its a room sealed boiler and no co is leaking into this room,no machine was used to do testing.
3,asked radiator man back to further investigate more and i will pay him,he takes out burner and finds heating exchanger is 90% blocked with deposits and fan is pushing fumes through rubber seal on burner box and not through to the flue.
so now he has turned it off again saying it needs a scraper to dislodge deposits and a gasket kit,he says its approx a 4 hour job.
so shall i call back british gas and complain,is it worth it.
bye for now.
the story so far.
1,had plumber changed all my rads fo newer and larger rads,no probs there.the plumber a corgi reg chap did a visual inspection of the boiler and was conserned about fumes.he took off front panel and used his tpi co meter and found co reading around where burner meets combustion box.he said readings was same as putting tpi meter down flue.
he asked me to discon it i agreed.signed his paperwork etc.
2.called british gas in as under maintaince contract.
bg engineer reconnects boiler restarts it and says its a room sealed boiler and no co is leaking into this room,no machine was used to do testing.
3,asked radiator man back to further investigate more and i will pay him,he takes out burner and finds heating exchanger is 90% blocked with deposits and fan is pushing fumes through rubber seal on burner box and not through to the flue.
so now he has turned it off again saying it needs a scraper to dislodge deposits and a gasket kit,he says its approx a 4 hour job.
so shall i call back british gas and complain,is it worth it.