Frizz as the the new expansion vessel needs connecting to boiler return as close as possible i would imagine the return should be in 22mm pipe so no real point in buying additional fittings to reduce down and back up again
Considering boiler internal connction between return and vessel is generally about 200-300mm and any where between 8-15mm connection,why do you think it needs 2m of 22mm.
If your figure is correct can you point to where it's stated or is it just an agiles rule.
The 2 metre rule applies to Solar simply because the temperature of the solar fluid can easily reach in excess of 100-130'c, this is beyond the rating of the diaphragm in the expansion vessel, so a 2 metre length of pipe (running downwards) is considered long enough to act as a cooling line to protect the vessel HOWEVER on a boiler running a 80'c and a return of around 70'c this is not an issue so the 2 metre rule does not apply.