Hi
Halstead Ace High (Combi) was losing pressure and the PRV was being activated every time I refilled it (to 1.3bar-cold). PRV is a 3.0bar PRV but pressure only ever went up to about 2.6bar, so it would seem it was being activated early.
I checked the pressure in the expansion vessel and it's 0.7 bar which is about right (no water came out either).
I removed the PRV and gave it a bit of a clean with a brush and some DS-3 I had lying around. Replaced everything and repressured the water back up to about 1.1bar.
Now the PRV doesn't seem to get activated and the pressure is sticking to around 1.1bar when cold (only been a day since I done it all) BUT the pressure when the heating is on only goes up to about 1.6bar. It has never gone up so little when the heating has been on, normally above 2bar, IS THIS OK? And why would that happen, does it make sense?
Thanks
Kelv
Halstead Ace High (Combi) was losing pressure and the PRV was being activated every time I refilled it (to 1.3bar-cold). PRV is a 3.0bar PRV but pressure only ever went up to about 2.6bar, so it would seem it was being activated early.
I checked the pressure in the expansion vessel and it's 0.7 bar which is about right (no water came out either).
I removed the PRV and gave it a bit of a clean with a brush and some DS-3 I had lying around. Replaced everything and repressured the water back up to about 1.1bar.
Now the PRV doesn't seem to get activated and the pressure is sticking to around 1.1bar when cold (only been a day since I done it all) BUT the pressure when the heating is on only goes up to about 1.6bar. It has never gone up so little when the heating has been on, normally above 2bar, IS THIS OK? And why would that happen, does it make sense?
Thanks
Kelv