I'll describe the whole setup.
There are in fact 3 gas boilers and a couple of gas hobs being fed from the single meter. The last to be installed was the boiler for the pool. The gas feed for this is taken directly after the meter and runs for about 100 feet in that standard yellow plastic pipe. It then goes to copper with the last two feet or so as 15mm.
Initially we suspected gas pressure, but this has been measured many times and it would appear that however many of the other appliances are on, it makes no difference to the ignition of the pool boiler.
Last night it started to go wrong again. Had been working faultlessly for three days.
The more I look and listen to the problem, I always seem to come back to a temperature problem. The ambient temperature around the boiler is 30 degrees C. I have strapped a temperature probe to the PCB and have been monitoring the rise and fall as the boiler goes through its various phases. With the boiler temp setting to about two thrids, the PCB sits at about 55 degrees C. If I take the side casing off, this drops by about 10 degrees. After the couple of bangs last night I left the PCB assembly totally exposed at the 45 degree position. This obviously keeps the PCB at the ambient room temperature. It then was OK.
The measured DC bias on the flame detector input was -6VDC dropping to about -30VDC when alight. Strange thing though, that leaving the probes connected, the flame detector did not work correctly. This is different from before.
A couple of things I will probably change:
1: The electrode gasket, is in good condition apart from the fact that it is now in two halves. Careful position though seems to make a good seal.
2: When the pool heat exchanger no longer requires heat, motorised valves shut off. This means that the pump, which is controlled by the boiler, is pumping against a dead end for the 3 minute run on time controlled by the PCB. The boiler temperature rises as it can't be pumped away. So maybe this ties in with the 6-7 minute off time I originally used for making it go wrong.
I was thinking of adding another motorised valve across the flow and return which turned on when nothing else required heat. That way the pump would never pump to nothing and any excess heat from the boiler could be pumped away.
Is this a good idea, or does it not really matter that the pump can hit a dead end for a few minutes.
Before I call out Potterton, I need to make absolutely sure that they can't blame some other part of the system for the fault. We have had numerous conversations with the technical dept at Potterton and although very helpful, one gets the feeling that once you have got past the "replace the PCB" or "replace some other component", their knowledge of the real in depth workings of this thing is limited.
I could really do with a copy of the circuit diagram of the PCB