Would welcome your views please. Please note that I have posted exactly the same question on another forum as I am keen to get as many views on this as possible - it seems to be a contentious issue!
Domestic property, TN-C-S described as PME feeding 10mm² to outside wall of house where it changes (inside IP rated box) to 3 core 6mm² SWA to outbuilding 25m away. SWA terminated in plastic box, no banjo fitted. Three cores carry on to plastic DB where only two cores are used as Line and Neutral. Outbuilding TT'd. MET of outbuilding DB connected to rod and to incoming copper water pipe. Other end of copper water pipe bonded to MET of house DB. In effect therefore, the outbuilding DB is connected to the house MET by the copper pipe and would suffer the same consequences as had the SWA and unused third core of the SWA been used to earth the outbuilding DB. How, under the regulations, should this situation be dealt with?
Thanks
Domestic property, TN-C-S described as PME feeding 10mm² to outside wall of house where it changes (inside IP rated box) to 3 core 6mm² SWA to outbuilding 25m away. SWA terminated in plastic box, no banjo fitted. Three cores carry on to plastic DB where only two cores are used as Line and Neutral. Outbuilding TT'd. MET of outbuilding DB connected to rod and to incoming copper water pipe. Other end of copper water pipe bonded to MET of house DB. In effect therefore, the outbuilding DB is connected to the house MET by the copper pipe and would suffer the same consequences as had the SWA and unused third core of the SWA been used to earth the outbuilding DB. How, under the regulations, should this situation be dealt with?