There is another way to approximately locate the short if the conductor shorting to ground or armour is still intact.
The conductor acts as the resistance track on a potentiometer and the voltage from the "wiper" at the fault is proportional to the distance along the cable to the fault.
Think of a potentiometer where the fault is the wiper mving along the resistance track formed by the Live conductor
The voltage drop along the Live conductor is linear between x and z and is equal to half of V loop as measured across Live and Neutral
The voltage on the Live at the location of the fault will via the fault affect the Earth conductor. If no current flows through the fault ( in purple ) then the two end of the fault resistance will be the same. Therefore the Earth conductor will be at the same voltage as the voltage on the Live at the lcoation of the fault.
Provided no current flows along the Earth conductor there can be no voltage drop along it. ( the meter take virtually no current ). Therefor the voltage at the end of the Earth conductor is the same as the voltage on the Live conductor at the location of the fault.
Read more: //www.diynot.com/forums/viewtopic.php?p=1894003#1894003#ixzz1ekURMvc1
The conductor acts as the resistance track on a potentiometer and the voltage from the "wiper" at the fault is proportional to the distance along the cable to the fault.
Think of a potentiometer where the fault is the wiper mving along the resistance track formed by the Live conductor
The voltage drop along the Live conductor is linear between x and z and is equal to half of V loop as measured across Live and Neutral
The voltage on the Live at the location of the fault will via the fault affect the Earth conductor. If no current flows through the fault ( in purple ) then the two end of the fault resistance will be the same. Therefore the Earth conductor will be at the same voltage as the voltage on the Live at the lcoation of the fault.
Provided no current flows along the Earth conductor there can be no voltage drop along it. ( the meter take virtually no current ). Therefor the voltage at the end of the Earth conductor is the same as the voltage on the Live conductor at the location of the fault.