JohnD said:Rather than FCUs I would have used 20A DP switches (same size but no fuse) with neons. This is because you have fuses in the 13A plugs, and the ideal number of fuses per appliance is ONE.
JohnD said:If you run more than two 13A appliances at a time on this circuit, the MCB will be overloaded and trip.
JohnD said:"more than two 13A appliances at a time"
mdbalson said:So the 20Amp MCB in the CCU should be made bigger
..An alternative would be to run a 4mm 32A radial, or a 2.5mm 32A ring.....
JohnD said:No, because your cable will not support a bigger load.
JohnD said:You will probably want to renovate the kitchen later and could incorporate a kitchen ring, chasing in all the cables and sockets horizontally at that time.
JohnD said:you could run it in 16mm mini-trunking