I don't quite follow your findings.
W, M and H surely stand for Water, Midway and Heating, which equate to bottom, midway and top, or top, midway and bottom.
So 'HW and CH off switch points to H'. Ok the valve stays in the last position when turned off, so being at H is understandable.
'HW on on its own switch, points to the top at M'. With no CH on and HW on demand the return spring should unwind the motor/valve/quadrant to the W position. not M, also M (midway) surely can't be at top
HW and CH on together switch is at midway W. It should be at midway if both are in demand, but midway is M.
CH only switch is back at H. This is correct and if boiler does not light then micro switch at fault.
The micro switch is mounted in the actuator head and I think you would be better getting the whole head replaced.
This type of fault will not allow CH on its own, when HW is called for with CH, the boiler is lit from the cylinder stat not the micro switch. so you do get CH, but only until the HW is satisfied and is cut off and the valve moves to CH (but does not light).
You can understand when there is CH at times it does become confusing. if the mecanics of the valve are not understood.
Another simple test with both HW and CH is to either (a) alter the cylinder stat to create a demand. Or (b) Run off some HW, which creates a demand.
You will find the boiler will light and you will get CH, but only until HW is satisfied.
W, M and H surely stand for Water, Midway and Heating, which equate to bottom, midway and top, or top, midway and bottom.
So 'HW and CH off switch points to H'. Ok the valve stays in the last position when turned off, so being at H is understandable.
'HW on on its own switch, points to the top at M'. With no CH on and HW on demand the return spring should unwind the motor/valve/quadrant to the W position. not M, also M (midway) surely can't be at top
HW and CH on together switch is at midway W. It should be at midway if both are in demand, but midway is M.
CH only switch is back at H. This is correct and if boiler does not light then micro switch at fault.
The micro switch is mounted in the actuator head and I think you would be better getting the whole head replaced.
This type of fault will not allow CH on its own, when HW is called for with CH, the boiler is lit from the cylinder stat not the micro switch. so you do get CH, but only until the HW is satisfied and is cut off and the valve moves to CH (but does not light).
You can understand when there is CH at times it does become confusing. if the mecanics of the valve are not understood.
Another simple test with both HW and CH is to either (a) alter the cylinder stat to create a demand. Or (b) Run off some HW, which creates a demand.
You will find the boiler will light and you will get CH, but only until HW is satisfied.