An update on this, I know people like to know the outcome.
Our friendly heating engineer did the alterations last summer, so now we have the combined F&E pipe tee'd in just before the pump as in the last diagram above - but we've left the open vents for now until we see how things are working.
At first I was a bit concerned that we were pumping over (and out of the open vents from the rads) as the pump started up as the level in the F&E tank would drop an inch or two when the pump started. In hindsight, I think this was just air being shifted around in the pipes - when you've a lot of 2" and 3" pipes, horizontal, it takes some time (literally weeks/months) to shift the air out of them. After a few months that issue appears to have gone - though it's hard to tell as I really need to be there when the system is cold and the pump isn't already running to see what happens when it starts up, and I'm rarely there in those conditions (at the moment, the pump is running nearly continuously on the frost stat).
So touch wood, things are now running sensibly. I've got the frost stats (air and pipe) configured to protect the system without heating the church all the time (as the single air stat was previously configured to do ) The burner is now sorted and doesn't seem to be suffering from airlocks (there was a small leak that was letting air in.) We've had a step built to stop rainwater running down the path from flooding the boiler room and burner There's a new bunded plastic tank. And with the mods done last summer, I think we now have a system that's not getting lots of fresh water all the time.
I've also altered the fan-coils so they have an extra low speed - added a switchable resistor in series with the low speed motor connection. That gets them to an almost inaudible level so in theory they can be left on during a service and still do a little bit to move air and keep the place warm. We just have to educate one person in particular not to go round switching them off a a matter of dogma - and that might take some doing (or just remove the switches )
Simon
Our friendly heating engineer did the alterations last summer, so now we have the combined F&E pipe tee'd in just before the pump as in the last diagram above - but we've left the open vents for now until we see how things are working.
At first I was a bit concerned that we were pumping over (and out of the open vents from the rads) as the pump started up as the level in the F&E tank would drop an inch or two when the pump started. In hindsight, I think this was just air being shifted around in the pipes - when you've a lot of 2" and 3" pipes, horizontal, it takes some time (literally weeks/months) to shift the air out of them. After a few months that issue appears to have gone - though it's hard to tell as I really need to be there when the system is cold and the pump isn't already running to see what happens when it starts up, and I'm rarely there in those conditions (at the moment, the pump is running nearly continuously on the frost stat).
So touch wood, things are now running sensibly. I've got the frost stats (air and pipe) configured to protect the system without heating the church all the time (as the single air stat was previously configured to do ) The burner is now sorted and doesn't seem to be suffering from airlocks (there was a small leak that was letting air in.) We've had a step built to stop rainwater running down the path from flooding the boiler room and burner There's a new bunded plastic tank. And with the mods done last summer, I think we now have a system that's not getting lots of fresh water all the time.
I've also altered the fan-coils so they have an extra low speed - added a switchable resistor in series with the low speed motor connection. That gets them to an almost inaudible level so in theory they can be left on during a service and still do a little bit to move air and keep the place warm. We just have to educate one person in particular not to go round switching them off a a matter of dogma - and that might take some doing (or just remove the switches )
Simon