Should they not be designed such that no serious damage would be done to the cutout at currents that did not cause the fuse to operate?As far as i know, the majority of faulty service heads that flash over are caused by overload/heating of the service.
Kind Regards, John
If you consider an installation, say a school, originally it was running fine on 3 phase 100A supply, probably drawing about 40A per phase.
Then a nursery is added to the school as well as a heated indoor swimming pool.
Then the school has to expand and they add 4 large portacabins. The council scrimped on the design and they are quite cold, so the school go out and buy a load of 2KW fan floor heaters but the electrician put all the sockets on 1 phase
Then because of the added children, the kitchen has to be expanded and modernized.
Because of the added children, more staff are employed and a teachers lounge is added.
A meter operator goes out one evening to exchange the meter and as part of his risk assement touches the L1 fuse holder and it is red hot, tails were clamped and L1 was sucking 109A, all the load is removed and the installation is allowed to cool down for 20 minutes, L1 fuse is firmly stuck and annealed into the holder.
DNO are called out and a hole is dug, cable cut, service head disassembled and found that all the pitch had leaked out of the cast iron head and the paper insulation has started to burn away. Meter operator is told he is very very lucky that a flash over had not acured, if he had tried harder and tugged on the fuse a bit harder, it probably would of given way and he would of got a big bang.
Now you may blame the electricians who added and added to the installation, you could blame the staff who stuck in a load of heaters, the head master for not stopping them, but this was all done over a period of 5 years and acording to them "we have never had a problem until you turned up".