Bit of help for me, if ya’ would……
Getting a few dodgy readings from a rod..
Ze = 488Ohms (gas / water disconnected)
Zs = 5.4 Ohms up to 9.3 Ohms various circuits (Avo LCB2000)
R1 + R2 Readings to circuits are 0.21 up to 0.54 (aint got paperwork in front of me)
Now I thought Zs = Ze + (R1+R2), not the case…….
The wiring methods were to be desired, but what would cause these readings? I cant see it picking up earth paths through the brickwork etc, gas & water bond was disconnected at time of test.
Also 100mA protecting circuits tripping around 43ms x1, so other calculation (just confirming)
Ra x Ia therefore 488 x 0.10 = 48.8V (less than 50V)
kA calculated, 230 / 488 = 0.47A (0.00047kA)
I dunno if its me, missing something obvious or the lads paperwork, or the tester is FUBAR……
Regards in advanced
Ian