davy_owen_88 said:Sockets reasonably expected to supply outdoor equipment must have 30mA RCD protection.
Hi again, so inside sockets do not? We do have an outside socket. Thanks
davy_owen_88 said:Any socket, inside or out that can be expected to supply equipment used OUTDOORS must have 30ma RCD protection. I suppose you could argue that since you have an outdoor socket that none of the indoor sockets will be used for outdoor appliances but I would always RCD protect all the socket outlets regardless.
JohnD said:What brand of consumer unit do you have; and which circuits are RCD protected? Do you have any spare ways?
plugwash said:it might if the sockets are only single pole and the fault is neutral-earth.
sometimes the only way to get to the bottom of intermittant RCD issues is to take a divide and conquer approach. Unfortunately this can get rather expensive.
if you have spare ways on the non-rcd side i would put a couple of RCBOs in there and connect the socket circuits to them. At best (if its a combination of many seperate leakages) this may solve your problem, if not it will at least give you more of a clue where to look.
JohnD said:I was thinking about RCBOs
For brand:
Each device will be marked (e.g.) B32 Hager or Wylex or crabtree or Volex or something - this is the rating of the MCB (the amps it can carry) and the makers name. If you can post a picture of the CU someone will recognise it.
http://www.diynot.com/forums/viewtopic.php?t=73320
Some of the circuits will be protected by the RCD and some will not - I gather from your reply that the ones on the RCD are Cooker, downstairs sockets, upstairs sockets, kitchen and outside sockets. So your lighting circuits and imersion heater are not on the RCD but seemingly everything else is.
It is quite common to have slight background leakage on circuits, and in this case, it takes very little extra leakage to push an RCD over the tripping boundary. The cooker and the washing machine are likely to have slight earth leakage on them; so are the dishwasher, fishtank heater, central heating boiler and pump, kettle and coffeemaker (basically anything with a heating element and/or water in it). So are any sockets, appliances or lamps outside as they may get damp from rain. If you UNPLUG all of these (not just switched of) you may find the nuisance tripping stops (the cooker should have a very large switch (but no plug) which will be adequate to isolate it)
lisac said:Hi again, I bet you think I've got an answer for everything
JohnD said:lisac said:Hi again, I bet you think I've got an answer for everything
Sure I have![]()
Including an answer I haven't told you about until I know more about your installation
earth leakages vary, so what trips one minute may not trip the next (especially if the current is made of several small leakages adding together). Even a rainy day can make it happen more often.
Intermittent trips can be very hard to track down.
Any chance of that photo?
probablly an intermittant fault in the washing machine.lisac said:Hi again, I bet you think I've got an answer for everything but I have tried unplugging everything, then plugging in the washing machine and it will trip. I do understand that a selection of appliances can have a small leakage that will when all plugged in cause it to trip, but like I said it happens with just the washing machine. I know it sounds like the machine but I can't understand why I can run a cycle without a problem if there is a leakage should it not trip everytime I switch it on?
JohnD said:Read that link. I use photobucket
http://s113.photobucket.com/albums/n228/JohnD_UK/?action=view¤t=stickyout1.gif[/QUOTE]
Thanks, ok lets give this a go! I've got two pictures for you. http://i202.photobucket.com/albums/aa59/lisac20/fuseboard2.jpg http://i202.photobucket.com/albums/aa59/lisac20/fuseboard1.jpg
Any good??
plugwash said:probablly an intermittant fault in the washing machine.lisac said:Hi again, I bet you think I've got an answer for everything but I have tried unplugging everything, then plugging in the washing machine and it will trip. I do understand that a selection of appliances can have a small leakage that will when all plugged in cause it to trip, but like I said it happens with just the washing machine. I know it sounds like the machine but I can't understand why I can run a cycle without a problem if there is a leakage should it not trip everytime I switch it on?