The electrician would probably welcome electrician's terms, rather than layman's ones What you need to ask him is to determine (by measurement) whether the "Earth Fault Earth Impedance" ('EFLI', also known as Zs) of the circuit is low enough to support a C20 RCBO - which, in case he doesn't know, since July 1st means that the EFLI must be no greater than 1.09 ohms.So i ordered a 20a hager rcbo type c after the first couple of replies but now wondering should i have lol.. Little in depth for me the replies above, Once the new rcbo get shere i'll contact a sparky and ask him to test if it will be ok, what do i need to ask him to do and why in layman's terms?
Kind Regards, John