3 fires?!!
if you had 1 fire 1 cooker and 1 boiler, you need to calculate each section separately.
Eg meter to boiler is furthest away and has most number of sections between meter and boiler, for eg 3. You work out length from tee to boiler (that own individual section, ie section b-c) and include all fittings, etc. Eg 1 metre plus 2 fittings, = 2M X 3 sections (max number) = 6M gas rate of boiler, eg 2.5m3/hr - from chart find next size up, prob 22mm would be easily suitable.
If the installation was THAT large, then it would be calssed as commercial probably anyway, total IV over 0.035m3.
if you had 1 fire 1 cooker and 1 boiler, you need to calculate each section separately.
Eg meter to boiler is furthest away and has most number of sections between meter and boiler, for eg 3. You work out length from tee to boiler (that own individual section, ie section b-c) and include all fittings, etc. Eg 1 metre plus 2 fittings, = 2M X 3 sections (max number) = 6M gas rate of boiler, eg 2.5m3/hr - from chart find next size up, prob 22mm would be easily suitable.
If the installation was THAT large, then it would be calssed as commercial probably anyway, total IV over 0.035m3.