Just to throw another question, or two, into the same pot; are you saying it is not legally required. If that is the case may I ask on what basis?
Firstly, there is nothing "legal" about it - the electrical regulations are not statutory - apart from Part P of the Building Regulations which states that, in domestic premises, all electrical work must be carried out to ensure safety.
Please not just according to personal thoughts.
No, just facts.
Earthing is not a good thing in its own right. It is a necessary evil for metal appliances and accessories so that, should they become live because of a fault, the protective device will open and disconnect the supply.
These metal items, are all connected together by their respective Circuit Protective Conductors (earth wires). Consequently, when one becomes live, because of a fault, they all do, for the short time until disconnection.
Any pipes connected to these same CPCs also become live during this short time.
Therefore any pipes NOT connected to these CPCs should NOT be connected to them by unnecessary Bonding (which isn't bonding, but unnecessary earthing).
Bonding is only required for parts
because they are already 'earthed' by some means - either the electrical installation or the ground.
Parts which have absolutely NO connection to any 'earth' of any kind must NOT be bonded or earthed - except, of course, the unfortunate metal bits of electrical equipment.
Bonding equalises the potential between earthed parts during such faults.
If you was asked to fir an earth connection would you advise customer they were wasting their money as you considered it unnecessary in their particular circumstances?
If you are talking about Main Bonding, as we have been, then it is NOT 'earthing'.
It is installed to equalise the true earth potential - where a pipe (an extraneous-conductive-part) is connected to the ground - and the installation earthing at the Main Earthing Terminal.
If any pipes entering the premises are not in contact with the ground (not e-c-ps) then they have no potential (different or otherwise) to equalise and are better left that way.
Actually most of thes pipes will be connected to the CPCs of boilers, immersions etc. (as above) so unnecessary bonding does not really matter - although it will do no good - but they might NOT be by virtue of plastic pipe inserts etc.