I can see the problem. Landlords have a bad reputation under tradesmen. As for myself, I won't go out for an absentee LL unless I get paid up front for the diagnostics.
Most good boiler engineers would know what a zenner diode does for example.
Tony
That doesn't make sense...
Earlier you said you disconnected the DHW switch assembly from the loom and the heating operated fine but the relays clicked.
Now you have cleaned up the DHW operating pin/dryed the switch and it all works ok.
Anyway, I would never re-use a diaphragm, you can't guarantee it will seal properly (it could start leaking at any moment). In addition the scaled pin will have damaged the PTFE/O ring in the cover gland.
I suggest the following parts are replaced....
cover 801201
diaphragm 801191
801189 switch
As mentioned earlier, the pcb requires checking/setting up. You don't have the knowledge or equipement to do this. Who carries out the annual gas safety check? You should not be repairing the boiler yourself. It's the landlords responsibility to find someone competent to do the job.
mickyg, the system won't let me pm??
mickyg, the system won't let me pm??
just added u as a friend, accept and try again