"""The radiators are working fine. It is not a flushing problem. Even though some of you don't want to believe that for some reason! """
Sylvian, its a very common problem that users cannot understand that heating will work fine in a very dirty system. The hot water delivery in a combi boiler depends totally on the operation of the plate heat exchanger.
Its very difficult for us to understand where the dirt on the secondary of the HE could keep coming from. Its fed ( we assume ) from the mains water which is usually clean!
You have not given us a clear answer to the question about the flow rate of hot water. If the secondary is blocked then the water will be very hot but the flow rate will be seriously reduced. Is this what you have.
Didn't the Glow-Worm engineer leave a job sheet saying what he thinks the problem is?
Tony