Right, follow this link if you don't have your manual.
http://www.glow-worm.co.uk/literature/
1st Lets confirm that there is definitely a blockage problem. On page 51, follow the instructions to access the D codes. With the hot tap running check D40 & D41 there should be no more than 20 ° difference. If greater than this there is definitely a blockage and we go to the next step.
2nd The instructions for the removal of the plate heat exchanger are on page 61; section 15.25. This is where you now take your pick of the many meethods of cleaning it. BTW there may also be a blockage on the filter shown in Diagram 15.20 - with the system drained it may be worth cleaning anyway, a stiff brush will do it.
Good luck
http://www.glow-worm.co.uk/literature/
1st Lets confirm that there is definitely a blockage problem. On page 51, follow the instructions to access the D codes. With the hot tap running check D40 & D41 there should be no more than 20 ° difference. If greater than this there is definitely a blockage and we go to the next step.
2nd The instructions for the removal of the plate heat exchanger are on page 61; section 15.25. This is where you now take your pick of the many meethods of cleaning it. BTW there may also be a blockage on the filter shown in Diagram 15.20 - with the system drained it may be worth cleaning anyway, a stiff brush will do it.