So here is the supplementary info now it seems to be adequate. Feel free to comment..... I know you won't hold back, but it's all helpful in its own way!
Single storey side extension and partial garage conversion into utility room and w/c
Foundations
C25 concrete mass fill to BS5328 (2)
To solid ground (approx 1000mm d x 600mm w)
External walls below DPC
7.3N 100mm concrete blocks
75mm Imperial frost resistant bricks
Weak mix cavity fill to 225mm below DPC
DPC 315mm above ground level
External walls above DPC
Outer leaf 7.3N 100mm concrete blocks with cement based render
Inner leaf 3.6N 100mm thermalite blocks non combustible euroclass A1 fire
Plasterboard and skim finish
Cavity wall rockwool slab 100mm non combustible euroclass A1 fire
Stainless steel wall ties set at 900mm horizontal 450mm vertical
Insulated cavity wall closures at all cavity openings
Catnic insulated cavity lintels 100mm at window and door openings
(U=0.3w/mK)
Doors & Windows
UPVc french doors 1800 x 2100, 28mm double glazed Low-e glass (U=1.4w/mK)
Windows to front 28mm double glazed Low-e glass (U=1.4w/mK)
Skylight 16mm argon filled approx 800 x 1200 with timber kerb to minimise thermal bridge (U=1.2w/mK)
Flat roof - Warm deck construction
GRP covering, 11mm OSB3 top deck, 100mm Celotex solid insulation, VCL, 18mm OSB3 base deck, Firrings to finished fall of minimum 1:80 as per BS6229 & BS8217, 200x50 Joists (4700 max span), 12.5mm plasterboard with skim coat
(U=0.15w/mK)
Floor - Solid construction
150mm compacted MOT, sand blinding, 1200ga DPM, 150mm GEN1 concrete slab, 100mm Celotex, Wet UFH, 40mm self levelling screed, 25mm PIR edge upstand to prevent thermal bridge, Tiled FFL. (U=0.22w/mK)
Plumbing and heating
Wet UFH system 200mm pipe centres, (100mm within 500mm of external patio doors) connected to combi boiler with room thermostat.
Hot and cold water feed to sink, utility and W/C
No gas work required
Drainage
Under ground
100mm PVC pipe, minimum 1:80 fall, 150mm pea gravel surrounding before backfill
Rodding eye located at top of straight runs
Above ground
40mm waste for sinks/washing machine/dishwasher connected to main sewer run
Electrics
To be carried out to Part P by electrician
Ventilation
Kitchen - Over hob, (minimum of 30l/s)
Utility - extractor fan (minimum 30l/s)
W/C - extractor fan with over run (minimum 6l/s)
In addition to purge ventilation
Lighting
LED low energy downlighting
Partial garage conversion
Floor, roof, drainage, electrics, lighting, ventilation, plumbing, heating to conform as above
Walls, single skin 100mm thermalite block with 60mm gyproc thermaline on dabs, skimmed (0.3w/mK)
Air leakage & thermal bridging
Constructed so that there are no reasonably avoidable thermal bridges in the insulation layers caused by gaps within the various elements, at the joints between elements and at the edges of elements such as those around window and door openings.