Hi all, got the photos.
Here is the main CU. The incoming supply is rated at only 80A and the meter is registered as being able to handle 80A. Incoming supply is switched using an 80A 100ma protected RCD. Fine.
http://i979.photobucket.com/albums/ae271/mbga9pgf/IMG_2717.jpg
RH side of the CU:
http://i979.photobucket.com/albums/ae271/mbga9pgf/IMG_2719.jpg
63A RCD protected at 30ma. Now, my issue is this. The main annex protection comes OFF the 63A side of the CU and not the 80A side. The annex has an electric power shower (about 7Kw) and wiring for the electric cooker. Not enough I reckon, as the Annex MCB is protected at 40A. With spots, cooker and shower on, its going to trip the CB.
Inside the annex, we have this:
http://i979.photobucket.com/albums/ae271/mbga9pgf/IMG_2727.jpg
40A supply protected by a 100a switch?!?! The CU is made my MK.
Thoughts? If I were to replace 7Kw power shower with a hot water mixer supplied unit instead and wired in the kitchen cooker power supply correctly, I cannot see the power supply being an issue. Personally, I would like to see a second supply or the current main house CU supply upped to 100a or above, at the same time they install the economy 7 meter...
The SWA I talked about previously trailing across the garden is photo'ed here
http://i979.photobucket.com/albums/ae271/mbga9pgf/IMG_2721.jpg
Not great and something I intend to sort. If I were going to up the supply to the annex, to say a 60A MCB using ducted 16mm wire, I have worked out that would be plenty for "worst case" expected usage, accounting for 3% voltage drop max across the wire length, wire raing etc Plus, neat tidy and no training wires across the borders.
Other issue:
Kitchen 2 way lighting wired incorrectly and only 2 core between the switches for the wiring. Is there an easy way of pulling out the 2 core and replacing with suitable 3 core to enable 2 way lighting without having to open up the wall cavity.
Does the main power supply to the light switch usually include an earth? at the mo, one switch at one end has the live, the other the neutral and the earth is simply attached from the switch to the switch housing rather than being connected to any earth wire....