Remove the sensor head, turn it to full then undo the silver ring and the sensor will pull off, if that stops the banging that valve is on the wrong way
Given the absence of arrows I would assume that's an old uni-directional valve and the flow may be going the wrong way through it...when the valve seat is near the closed position it slams shut causing the noise.
Put the heating on, the pipe entering the valve should become hot before the other radiator pipe.
I've used sealant on many occasions and with older boilers it has never been a problem. Given the choice of digging up concrete floors and tearing apart the house 90% of customers except the risk and go for sealant and it often does the trick.
It will only kake a few seconds no tools needed, or as the hammering is happening open the valve up full to see if it stopsHi, the valve is the way it's always been. I was here when the cowboy was here and he didn't do anything with the valve.
Hi, the banging starts when the valve is open, turning the valve to the off position stops it.It will only kake a few seconds no tools needed, or as the hammering is happening open the valve up full to see if it stops
I did, on the advice of the so called tradesman , wish I hadn't nowSurely you choose the cheaper option of going for sealer rather than locating the leak?
I know. The fella who came was a one man band from trust a trader. I should have heard the alarm bells when he said he could come within the hour. Just thought if i called a heating "company" at least i would feel comfortable calling them back if there were any subsequent problems. Will try the see which pipe heats up later when I get home. ThanksI've used leak sealer many times when it's impractical to dig up concrete floors etc. I wouldn't recommend it with new boilers (or those on warranty) but it rarely causes problems.
I can't really see how the leak sealer and a knocking rad valve are related unless the spindle is leaking perhaps.
Put the heating on and tell us what pipe warms first.
You're not really in any position to ascertain whether the next heating eng. is any better than the last so you may as well do a little investigating.
I've used leak sealer many times when it's impractical to dig up concrete floors etc. I wouldn't recommend it with new boilers (or those on warranty) but it rarely causes problems.
I can't really see how the leak sealer and a knocking rad valve are related unless the spindle is leaking perhaps.
Put the heating on and tell us what pipe warms first.
You're not really in any position to ascertain whether the next heating eng. is any better than the last so you may as well do a little investigating.
Hi Andy, no idea where the leak was/is. He didn't really spend any time looking for it . I'm thinking of getting a track and trace company or a heating engineer.Just because he came 'within the hour' does not mean anything. He could of being passing by or on his way to or from anotherr job.
Do you know where the leak is?
Andy