Sorry this is a bit long but really would like some answers before I go back to work tommorow!!
I was asked to check out a tripping RCD fault. On arrival she told me that it will trip anytime, no specific appliances are ever on at the time etc. It even trips in the middle of the night.
Got the megger out, all circuits were ok-ish, about +4meg ohms neutraul and live to earth, apart from one labeled sockets office and utility - these at the time read 0.8M - (the RCd was staying in whilst I was there.)
In the office there was loads of computer equipment, home cinema equipment etc etc... all pluged into one extension lead and in one socket. Pulled this out and got the poor reading on this equipment. The circuit then went up to abouit 4M as well. Tested each individual applicance nothing was particularly bad but I think a few faults combined were bringing it down to 0.8M.. old the customer that its prob ebst to have a dedicated office ring with T-bar sockets installed not on the RCD.
Am I correct in thinking that computer equipment will leak to earth ({had the figure of about 3mA per computer)? The RCD was also tripping at 18mA according to the ramp test.
I put the fault down to too much computer equipment being on the 30mA RCD.
Boss doesnt think this can be right and that I have missed something...
What do you think? Thanks!
I was asked to check out a tripping RCD fault. On arrival she told me that it will trip anytime, no specific appliances are ever on at the time etc. It even trips in the middle of the night.
Got the megger out, all circuits were ok-ish, about +4meg ohms neutraul and live to earth, apart from one labeled sockets office and utility - these at the time read 0.8M - (the RCd was staying in whilst I was there.)
In the office there was loads of computer equipment, home cinema equipment etc etc... all pluged into one extension lead and in one socket. Pulled this out and got the poor reading on this equipment. The circuit then went up to abouit 4M as well. Tested each individual applicance nothing was particularly bad but I think a few faults combined were bringing it down to 0.8M.. old the customer that its prob ebst to have a dedicated office ring with T-bar sockets installed not on the RCD.
Am I correct in thinking that computer equipment will leak to earth ({had the figure of about 3mA per computer)? The RCD was also tripping at 18mA according to the ramp test.
I put the fault down to too much computer equipment being on the 30mA RCD.
Boss doesnt think this can be right and that I have missed something...
What do you think? Thanks!