heatmiser neostat wifi
9 Jun 2014
Yorkshire
Has anyone had an issue with the neostat switching on an immersion tank ?
My neostat is communicating through the wifi, but the unit is not able to switch the immersion on.
It is wired into a contactor which then goes out to the immersion spur. The contactor is working ok as the neon light on the spur comes on when you artificially trigger it.
i'm sending the neostat back and hope to get a replacement. Just wondered if there was any issue with these units.
The Heatmiser neoStat hw is not suitable for switching an immersion heater on. It is only rated at 3A MAX
An immersion heater is rated at 13A so the contacts have probably been destroyed as they will have been grossly overloaded. If you do get a replacement and use it, the same thing will happen again.
I know this and so you use a contactor between the two which we have done. HM say this is correct
Using a contactor is fine. Sorry, when I read that I assumed that by "contactor" you were referring to the switching contacts inside the Heatmiser. Often incorrect terms are used (eg immersion tank ;)) so, I thought that was the case with the contactor.
Was the wiring connected like this:
1. The mains supply from the spur went to Heatmiser terminals marked mains L & N
2. You linked together, mains terminal L and C
3. NO goes to the contactor coil live, and N to the contactor coil neutral
4. The live to the immersion heater is fed via the contactor er.... contacts
Did the Heatmiser display show Timer On?
Did the contactor operate?
I checked the wiring with HM and he said it was correct
The HM display was saying it should be working but it wasn’t switching.
We tested the contactor by taking a wire out of the stat and putting it in with another cable. This brought on the neon light on the immersion spur so the contactor is working.
I am sending it back and hope it is a faulty switch
Thanks, let us know what happens please. Then if someone else has the same issue and reads this post it may be useful for them.
