shoild we take this into the combustion chamber?
Each sections effective length is multiplied by the number of sections , if the OP had a gas fire added then this would be 3 sections.
You have lost me with that too.
Can you explain in simple language and say why too?
so 50m @ 33.77 m3/hr .
Yeah that is true, but not what was expressed, or intepreted...
I would not have used those words either!
From the meter to the first branch 28mm.
From the first branch to the cooker 15mm.
From the first branch to the boiler 22mm.
That assumes the range is 15kw and not 5kw which is unlikely to be right.
I may be mistaken, but I always thought that the 1mb allowable drop was from the meter to the device, i.e meter to boiler, or meter to range.If we were to take the OP's example then we have 2 sections , ie:.....
A to B (meter to first tee)
B to C (first Tee to boiler) or B to D (first tee to range)
1 mb /2 = .5mb...each section should have a pressure drop not exceeding .5mb.