- Joined
- 11 Jan 2004
- Messages
- 45,906
- Reaction score
- 3,523
- Country
Where?
That no longer exists. Indeed, none of Chapter 61 exists any more. I suspect that you might me talking about ....612.3.1
If so, I would take "the earthing arrangement" to refer to the installation's CPC system, including MET, whether or not that was connected to actual 'earth'.BS 7671_2018 said:643.3.1 The insulation resistance shall be measured between live conductors and between live conductors and the protective conductor connected to the earthing arrangement.
Since you mention confusion, I have to say that I'm a bit confused by (uncertain of) what you are saying there (in relation to IR testing). Could you perhaps clarify?Not sure about the confusion, it wouldn't be a proper test if the cpc want connected to the earthing and bonding. ... if there was a fault between a live conductor and some metalwork in the house with a path to the main earth as the MCB or RCD would go as soon as the circuit was energised.
'Not connected' to what? I don't think there has ever been any suggestion that CPCs (if present) wouldn't be connected to the MET - Risteard's assertion appears to be that having CPCs/MET connected to ('true') earth is a "fundamental requirement" for IR testing.Of course one could do all the tests with the cpc not connected and then do separate ones from live conductors to the MET but that would be extra work.
Fair enough. I have to concede that you have identified one type of situation in which an IR test 'to earth' (rather than 'to CPCs') would theoretically be required.Well if there wasn't a true earth connected to the MET, what would happen if a live conductor was sitting in a puddle under the house. Unlikely on a new circuit just installed, but true earth is something that should probably be connected for the IR test.
Yes, sorry it's been renumbered. Earthing arrangement is not open to interpretation. It clearly requires the Earthing conductor to be connected during the test. The reasons are fairly obvious too, and cannot be considered anything other than an eminently sensible requirement.That no longer exists. Indeed, none of Chapter 61 exists any more. I suspect that you might me talking about ....
After all, although I realise that some 'requirements' of the regs are seemingly rather daft (and that some people feel constrained to comply with daft regulations), there is no electrical reason I can think of for requiring anything to be 'earthed' during IR testing - which is probably why I have never really interpreted the above to be imposing such a 'requirement'.
Fair enough, but if you are going to post references which consis of just a reference number, without any explanation, one might hope that you would ensure that the number was correct in terms of current regulations.Yes, sorry it's been renumbered.
Following John's post, I have have agreed that it would make a difference in an extremely improbable set of circumstances, but I have to say that I have yet to think of a way in which the situation could/would actually arise in the real world. As I've said, it would only happen if (all layers of) the insulation of a live conductor were somehow compromised, if that compromised insulation resulted in an electrical path to 'true earth' (e.g. wet soil - but not a bonded extraneous-c-p) and that no associated CPC, armour, metallic sheathing etc. was also involved in this fault. Even deliberately engineering such a situation would be far from simple....It clearly requires the Earthing conductor to be connected during the test. The reasons are fairly obvious too, and cannot be considered anything other than an eminently sensible requirement.
I think that either he or you have probably got the terminology a bit wrong. As I understand it, only local authorities can issue "Compliance Certificates".I'm not an electrician but in a property I refurbished the spark disappeared and another one came on the scene. He fixed all the bodge of the previous one, tested the whole lot and issued the landlord with a certificate of compliance (I'm sure that's how it called it).
An electrician can certify all the work he/she has done (e.g. 'fixing faults'), including relevant testing. An electrician can also undertake an Electrical Installation Condition Report (EICR), which involves inspecting and testing all/most of the installation and issuing a report on the current state of the installation (including recommendations for any remedial work which is either required or 'recommended').So shouldn't an electrician be fixing the faults, testing the system and then certify that it's safe despite not being entirely new?
In fairness I was asked for a Regulation number when I hadn't a copy of the Regs book on me. I don't carry it round with me.Fair enough, but if you are going to post references which consis of just a reference number, without any explanation, one might hope that you would ensure that the number was correct in terms of current regulations.
In any event, as I've said, it's almost a hypothetical discussion since (despite this thread), installations with no earth are very uncommon and, even when they are occasionally encountered, it's very unlikely that anyone would contemplate IR testing before addressing the earthing issue.
I thought you said you didn't have one because you couldn't afford it.In fairness I was asked for a Regulation number when I hadn't a copy of the Regs book on me. I don't carry it round with me.
Wrong way round:As I understand it, only local authorities can issue "Compliance Certificates".
I think that was in relation to BS 7288 (in another thread).I thought you said you didn't have one because you couldn't afford it.