Now that you have established the position of the return sensor, its more than likely that its reading correctly, strange that the circ pump stops though as it shouldnt during recycle conditions, next time you are doing a few tests check the S status parameters. Also the burner shouldnt cut out at its target temperature of 75C, it should rise to 80C but if the rate of rise is very rapid, easy to miss. I have read of several Vaillant owners where the burner is cutting out at only a few degrees above the target temp but this isnt your root problem.
If you assume the average boiler heat demand is say 8hw, just below its minimum output of 9kw, then assuming the rad returns at 33C and a 75C/70C boiler flow/return will mean that the circ pump flowrate is 22.93LPM of which 20.2LPM is recirculating and only 2.73LPM is circulating through the rads, normally one would expect ~ a dT of say 15C through the rads or a circ flow of 1.0LPM/kw of rad output so the rad circ rate should normally be at least 8LPM for that 8kw output.
thanks so far for the input, I have recorded 2 vids to show how the temp is rising
I have put links to one drive as they are too big the link will expire in few days should be enough to watch it
Error
mietek-my.sharepoint.com
what I notice when I set the flow temp lower to 60 the initial raise of the temp was more stable and the boiler didn't cut off quickly, but then the flow temp is set to 75 the raise was quick on pump set to auto and then it cut off at 80, drop the flow temp to 44 and then burner kick in again , I then changed the pump to 100% and it was raising up better. (the reason why I have flow temp higher is I have hot water tank and it feels warmer with struggling radiators in winter I'm sure once the issues are resolved it can be set lower)
I'm still not sure about this return temp d41 as its always 5 degree lower then flow temp, I have jump through d40 and d41 on the video to show, the sensor position explain why it shows higher reading and most likely it working correctly but I don't know why the return water is hot inside the boiler but is not coming back from radiators, is this the bypass and if yes what could be causing it and should it be behaving like this?
edit;
I have done another couple vids and one 7 min long to show that even with lower temp it will cut off it will just do it slower, with higher temp it just goes there faster and the speed of this happening is faster.