Hi guy`s and gal`s Just a quicky really ....
Just tested my TN-C-S system for my external earth fault loop ,(Ze) and got a high reading of 6.92 ohms,which is obviously high compared to to stated 0.35 ohm maximum.
Noticed the original main earth is only 10mm. If i change it for 16mm will this bring my high reading down or should i conntact my local supplier?.
Also noticed the meter tails from meter to my old connsumer unit are of the old braided coated type and only look approx 10-12mm dia,so would this give me a high reading?.