Nothing like leaving it to the last minute ay?
So NICEIC domestic installer inspection on Monday morning. 1st job to show is the work I've done at my own property! of course that means that until now I've not done anymore than the basics. r1 +r2 on the circuits I've touched and an RCD test when I powered up. no schedule of results, no Ze test, no PFC etc. thought id better get it sorted this afternoon!!Bad form I know but its my own property and theres always something better to do!!!
Ze came in at 0.02!
PFC at 19.9 KA this is as high as my 1552 will measure.
supply transformer is less than 100 yards away which explains the reading.
Ive read so far that its fine to leave the 6KA breakers in because I can use the 33KA of the 1361 main fuse.
Anybody know if this is definitely NOT OK? if There is someone out there who really thinks I need to do something about it then let me know and also if you think the inspector will be alright with it.
Anybody know what these inspectors are like? Im beginning to worry now!!!
Thanks
So NICEIC domestic installer inspection on Monday morning. 1st job to show is the work I've done at my own property! of course that means that until now I've not done anymore than the basics. r1 +r2 on the circuits I've touched and an RCD test when I powered up. no schedule of results, no Ze test, no PFC etc. thought id better get it sorted this afternoon!!Bad form I know but its my own property and theres always something better to do!!!
Ze came in at 0.02!
PFC at 19.9 KA this is as high as my 1552 will measure.
supply transformer is less than 100 yards away which explains the reading.
Ive read so far that its fine to leave the 6KA breakers in because I can use the 33KA of the 1361 main fuse.
Anybody know if this is definitely NOT OK? if There is someone out there who really thinks I need to do something about it then let me know and also if you think the inspector will be alright with it.
Anybody know what these inspectors are like? Im beginning to worry now!!!
Thanks