- Joined
- 11 Jan 2004
- Messages
- 43,990
- Reaction score
- 2,894
- Country
Nor did the old rule 'always test RCDs with the loads disconnected' until one failed on 1x and 5x, disconnected a refrigeration load and it was well within spec (was a brand new Schneider RCBO so it should bloody well pass!)
Yeah, I had that too. Funnily enough with an old MK CU.
It failed 1/2 x test and the Zs was too high, but when tested in isolation, it flew through the tests.