Does anyone have a photo of the wiring from a hive receiver to a Vaillant ecotec 837 (or similar) please? The boiler end is the bit I'm struggling with...
Thanks.
Does the boiler already have a room thermostat wired in?
If not there’s a problem as you would need to access a part of the boiler that isn’t recommended for the likes of you and me.
Does the boiler already have a room thermostat wired in?
If not there’s a problem as you would need to access a part of the boiler that isn’t recommended for the likes of you and me.
If you post a picture of the existing receiver and its wiring or a diagram of the connections someone will help. The required wiring will almost certainly already be available from the boiler end.
Is the Hive the single channel (heating only) model?
OK Brown goes to Hive Live L
Blue to Neutral N
Black & Grey can go either way round into Hive 1 & 3.
The thermostat switching is operating on the low voltage section of the boiler which would be wrecked if any mains voltages were applied to Black or Grey.
That's why I asked if it was a single channel Hive (which is OK) and you should ignore any instructions in the manual that suggest linking Live to any of the other terminals..