Honeywell BDR91 to Hive

Sponsored Links
So just wired the system up again and thought I would try pressing the hot water boost button. The boiler fires up. This shouldn’t do this though as it’s wired up for the single channel?

what’s your thoughts on this?
 
So just wired the system up again and thought I would try pressing the hot water boost button. The boiler fires up. This shouldn’t do this though as it’s wired up for the single channel?what’s your thoughts on this?

Post a photo of receiver please. Has it been setup wrong in menu? Boost on thermostat?
 
I have a Worcester combi boiler so just using the single channel.
You plonker no wonder it is not working , you have a DUAL channel Hive not the single channel as you said, Brown wire from 3 gets moved to 4 and the grey wire in 1 gets safely isolated as the dual channel has internal links this is not needed, if that doesnt work put the grey wire in 4 and isolate the brown wire
 
Last edited:
Sponsored Links
You plonker no wonder it is not working , you have a DUAL channel Hive not the single channel as you said, Brown wire from 3 gets moved to 4 and the grey wire in 1 gets safely isolated as the dual channel has internal links this is not needed

That’s what I was trying to get to with my above post :D
 
Last edited by a moderator:

DIYnot Local

Staff member

If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

Select the supplier or trade you require, enter your location to begin your search.


Are you a trade or supplier? You can create your listing free at DIYnot Local

 
Back
Top