Would that work when you released the push switch?
Tony
All you need to do is remove the voltage from the grey wire for a few seconds. Turn HW ON, count to 5, turn HW OFF.
There will always be voltage on the grey wire after HW has been turned off by timer or stat. It just needs to be interrupted so the spring starts moving the valve back to the HW position. This causes one of the switches in the valve to flick over, so the voltage from the grey wire is no longer applied to the motor.That won't work every time. If you turn the HW 'on' and the cylinder thermostat is satisfied, that will keep the live on the grey wire.All you need to do is remove the voltage from the grey wire for a few seconds. Turn HW ON, count to 5, turn HW OFF.
It would only be interrupted for milliseconds as the programmer's changeover contact switches from being directly connected to the grey wire, to being connected to the grey wire via the thermostat. I doubt that this would give enough time for the motor to move sufficiently.It just needs to be interrupted so the spring starts moving the valve back to the HW position.