7 ---> 3
6 ---> 5
5 ---> Live
Based on the above wiring links and following the circuit through the switches shown on the ST699 diagram, it appears that you have an old system where the hot water is operated by gravity circulation and the heating by a pump. So whenever the boiler is on (for heating or hot water) the water gets hot by natural circulation of hot water rising up to the hot water cylinder. When the pump is started the radiators then heat up as well.
So this gives rise to an installation where the hot water setting controls the boiler, and the heating setting the pump. The problem is that for the heating to operate both settings have to be 'on' together so that both the boiler and the pump are running.
The above links ensure that whenever the pump is switched 'on' (for Heating) the boiler is also switched 'on' even if the hot water was set to be off.
The pump would have been wired to terminal 3, and the boiler terminal to 8
However, the ST9400C has a facility that is created by the links built in. So the pump would be wired to Heating ON and the Boiler to Hot Water on with it set to operate as a mini programmer using the special selection switch. Therefore any external links are not required.
With it set to Mini Programmer mode, the wiring for the ST9400C would be
N Neutral
L Live
1 Not used
2 Not used
3 Boiler Live (This was the wire in ST699 terminal 8.)
4 Pump Live (This was the wire in ST699 terminal 3.)
Some boilers, but not all also need a permanent live supply, so that's the wire shown dashed. If it was there before it needs to stay. Earths are omitted for clarity but should be maintained.