No this engs. another clueless wonder
You've got nearly a 50% drop in flowrate through the boiler...so there's a problem. Of course there's will be a drop in water flowrate after going through the boiler but not to that extent.
Burner modulation and the temperature control on these is never that great, but if you set the temp control to a low setting the burner should modulate up and down and finally settle at a low rate.
"He said it should increase the water temp by about 35 degrees" Load of carp
Manufacturers specify the performance of their combis by qouting a hot water flowrate raised by 35 degrees (sometimes 30 or 40 degrees too). The boiler itself will attempt to heat the water to the target temperature setting on the front of the boiler but if the flow's too great it won't achieve that, and if the flow's to little once it gets around 60 degrees it will modulate down and shut off the burner. The boiler does not understand a 35 degree difference Unfortunately there are many "engineers" that can't understand this either
You've got nearly a 50% drop in flowrate through the boiler...so there's a problem. Of course there's will be a drop in water flowrate after going through the boiler but not to that extent.
Burner modulation and the temperature control on these is never that great, but if you set the temp control to a low setting the burner should modulate up and down and finally settle at a low rate.
"He said it should increase the water temp by about 35 degrees" Load of carp
Manufacturers specify the performance of their combis by qouting a hot water flowrate raised by 35 degrees (sometimes 30 or 40 degrees too). The boiler itself will attempt to heat the water to the target temperature setting on the front of the boiler but if the flow's too great it won't achieve that, and if the flow's to little once it gets around 60 degrees it will modulate down and shut off the burner. The boiler does not understand a 35 degree difference Unfortunately there are many "engineers" that can't understand this either