So I shouldn't be too concerned at not testing these few fittings at 18bar?
No. I wouldn't lose sleep over it!
So I shouldn't be too concerned at not testing these few fittings at 18bar?
So in my situation a may be better with hep2o. I ve use polyplumb and never had a problem before though. Are polyplumb saying 18 bar is.needed.for.the grab ring to fully bite? Or to make sure.the fitting is all the way in? I always witness mark the pipe.so know.its.fully in the.fittingThe difference in test pressures is correct.
Polyplumb is an "O" ring first fitting, as was the very first Hep2o fittings and the Hep2o "Slimline" fitting.
The last 3 versions of Hep2o have all been "Grab" first, what this means is that in the Polyplumb fitting the pipe passes through the "O" ring first and then through the "grab" ring, so if the pipe isn't inserted fully the "grab" may not be fully engaged and the possibility of a "full bore blow off" hence the higher test pressure of 18 bar.
With the "grab" first fitting, if not fully inserted you will not get a "full bore blow off" but a leak, with this type of fitting the recommendation is 1.5 times the maximum working pressure.
It is generally accepted that the "O" ring first type of fitting is more prone to "installer error"
So in my situation a may be better with hep2o. I ve use polyplumb and never had a problem before though. Are polyplumb saying 18 bar is.needed.for.the grab ring to fully bite? Or to make sure.the fitting is all the way in? I always witness mark the pipe.so know.its.fully in the.fittingThe difference in test pressures is correct.
Polyplumb is an "O" ring first fitting, as was the very first Hep2o fittings and the Hep2o "Slimline" fitting.
The last 3 versions of Hep2o have all been "Grab" first, what this means is that in the Polyplumb fitting the pipe passes through the "O" ring first and then through the "grab" ring, so if the pipe isn't inserted fully the "grab" may not be fully engaged and the possibility of a "full bore blow off" hence the higher test pressure of 18 bar.
With the "grab" first fitting, if not fully inserted you will not get a "full bore blow off" but a leak, with this type of fitting the recommendation is 1.5 times the maximum working pressure.
It is generally accepted that the "O" ring first type of fitting is more prone to "installer error"
These are our fittings of choice, having tried and tested them all. Just be aware, you'll need the tool for deconstructing them and if too close to another fitting, you'll never get them off, but they give you real confidence!
http://www.wavin.co.uk/web/solutions/potable-water/plumbing-systems/pushfit.htm