If that's 130 to 222 on the last 3 digits on the meter that's a bit low(29.5kW input I make it). Maybe the boiler is cutting itself down because it thinks it's hot enough, but 70 isn't high enough for that.
70 in , 60 out
6 in, 25 out
Would have expected better transfer than that.
19 degree rise on 10 l/min is 13.25kW.
a) ??? primary side of main heat exchanger scaled (too much energy is going up the flue, (29.5 / 35.5) * 26.6 = 22.1kW)
b) ??? primary temperature sensor (70 is too low)
c) ??? gas valve pressure (worth checking)
d) ??? primary side of secondary hex scaled up (Inadequate transfer)
Which type of HEX is it??
70 in , 60 out
6 in, 25 out
Would have expected better transfer than that.
19 degree rise on 10 l/min is 13.25kW.
a) ??? primary side of main heat exchanger scaled (too much energy is going up the flue, (29.5 / 35.5) * 26.6 = 22.1kW)
b) ??? primary temperature sensor (70 is too low)
c) ??? gas valve pressure (worth checking)
d) ??? primary side of secondary hex scaled up (Inadequate transfer)
Which type of HEX is it??