If you want to spend money on better control for this boiler (Ecotec Pro28), you'd probably be better off with the VRC 400 controller, which will automatically adjust the boiler Flow temperature according to the external temperature (ie. it's a weather compensator). You won't be able to do much more about the Return temperature except minimise the flows through individual rads by winding down the lockshields, as already suggested. Unfortunately, the Pro28 only has a single-speed pump, so cannot modulate the flow rate itself.
At least with a weather comp,the Flow temp will be adjusted to the minimum required to warm the house, so for 25% of the heating season at least (given warmer winters!), the Flow will be at 65 or less, giving a good chance that the Return will be 55 or lower, so the boiler will condense.