I just fitted Honeywell DU144 auto bypass valve to my central heating system (open vent s plan system). I have found the manual for my Grundfos pump (selectric):
http://www.screwfix.com/sfd/i/cat/pdfs/01/p3983301.pdf
and the manual for my bypass valve:
http://www.screwfix.com/sfd/i/cat/pdfs/50/p4734550.pdf
My GlowWorm Energysaver60 boiler specifies a minimum flow of 17l per minute. This translates to 0.28l per second or 1020l per hour.
My problem is this, I want to run my pump on speed setting 2 (as it creates plenty of heat in all radiators and is nice and quiet at this speed).
The table provided in the pump manual suggests that 0.28l/s translates to about 2m of head at speed setting 2.
The bypass valve manual then suggests that for 1020l/h and 2m of head (200mB), there is no appropriate setting on the bypass valve.
Am I reading this correctly? Have I bought the wrong type of valve?
Cheers,
iep