New here and sorry for digging up old post. Fitting a hive mini to a i29 c volkera, which terminals do i use and I need to remove the bridge from 1 and 2. The 2 wires from the mini do they need to be connected in any order 3 to 3 and 4 to 4 for instance.
New here and sorry for digging up old post. Fitting a hive mini to a i29 c volkera, which terminals do i use and I need to remove the bridge from 1 and 2. The 2 wires from the mini do they need to be connected in any order 3 to 3 and 4 to 4 for instance.
The link wire needs to be removed from the TA terminals on X11.
You must only connect the TA terminals to the volt free contacts - terminals 1 & 3 (it doesn't matter which order), on a single channel Hive.
Do not make any other links on the Hive, that you may see in other wiring diagrams.
The Hive will then need to be powered from a separate mains flex, connecting to the L, N and earth terminals.
The link wire needs to be removed from the TA terminals on X11.
You must only connect the TA terminals to the volt free contacts - terminals 1 & 3 (it doesn't matter which order), on a single channel Hive.
Do not make any other links on the Hive, that you may see in other wiring diagrams.
The Hive will then need to be powered from a separate mains flex, connecting to the L, N and earth terminals.
No, I'm afraid not! - that's the dual channel Hive.
Connecting that to TA would damage the boilers PCB and would lead to expensive repairs.
You need the single channel Hive, or "Hive Mini for Heating".
If you need to find a tradesperson to get your job done, please try our local search below,
or if you are doing it yourself you can find suppliers local to you.
Select the supplier or trade you require, enter your location to begin your search.
Please select a service and enter a location to continue...
Are you a trade or supplier? You can create your listing free at DIYnot Local