314.1 incoming!
Once the RCD is fitted alongside the retrofitted MCB's will the consumer unit then be to current regs?
It won't matter how close together the sockets are, or what cable is used, or how the cable is installed.
All socket outlets require RCD protection.
411.3.3 Additional protection
In a.c. systems, additional protection by means of an RCD in accordance with Regulation 415.1 shall be provided for:
(i) socket-outlets with a rated current not exceeding 20A that are for use by ordinary persons and are intended for general use, and
(ii) mobile equipment with a current rating not exceeding 32A for use outdoors.
An exception to (i) is permitted for:
(a) socket-outlets for use under the supervision of skilled or instructed persons, e.g. in some commercial or industrial locations, or
(b) a specific labeled or otherwise suitably identified socket-outlet provided for connection of a particular item of equipment.
It won't matter how close together the sockets are, or what cable is used, or how the cable is installed.
All socket outlets require RCD protection.
It won't matter how close together the sockets are, or what cable is used, or how the cable is installed.
All socket outlets require RCD protection.
Oops, yea i was thinking 'rcd for buried cable' and a cheaper way of dealing with it.
kinda overlooked the 'its for sockets' bit.
To the OP,
Do you need 4 socket outlets in every corner? Would 3 be enough?
http://www.screwfix.com/prods/12362...s/Clipsal-Converta-Skt-2G-to-3G-Polycarbonate
just a thought