I would recommend doing some tests before replacing the valve head, the motor must be working so the problem is either microswitches in the valve head faulty, mechanism in valve head faulty, or problem with the wiring to the valve.
At the very least carry out this test to avoid wasting money on an unneeded new valve head.
With hot water off at the programmer and central heating on with room stat turned up, you should have:
240V on the valves white wire
240V on the valves grey wire
If you don't have the above, the fault is external to the valve.
When it's all working there should also be 240V on the valves orange wire to power the pump and boiler, this probably isn't happening at the moment.
All tests will need to be carried out with a 2 probe AC volt meter, with one probe connected to neutral for all tests. A neon screwdriver or volt stick is not suitable and will give incorrect/misleading readings.
I'm going to guess there is no power to the grey wire when the hot water is off.
I never even got to open the connection box as when I moved it from under the floorboards in the airing cupboard the heating burst in to life. I'm guessing (hoping) that there is a loose connection in there somewhere but I'm not going to touch it just yet as the house is warming up and we're sitting at 15c with blankets on. If it goes off again at least I'll have a starting position.
How can something so simple cause so much work?
Thanks you all for the help