Hi Gordongas, Namsag,
Having followed your advice, I think I'm very close!
I removed each GREY wire in turn (CH & HW turned OFF at timer but pump was still running). The pump stopped when the Danfoss MV grey wire was disconnected (and kept running when Honeywell grey wire was taken out). Am I right to conclude that it's the Danfoss microswitch that is faulty and therefore needs replacing?
Many thanks!
Anya x
Having followed your advice, I think I'm very close!
I removed each GREY wire in turn (CH & HW turned OFF at timer but pump was still running). The pump stopped when the Danfoss MV grey wire was disconnected (and kept running when Honeywell grey wire was taken out). Am I right to conclude that it's the Danfoss microswitch that is faulty and therefore needs replacing?
Many thanks!
Anya x